Old 03-18-2024, 02:38 PM   #1
lindy46
Member
 
Join Date: Apr 2013
Location: Tennessee
Posts: 65
Water heater pressure relief dripping

The pressure relief valve started dripping, so I cleaned and sprayed it with WD40. Still leaked. So I bought a new unit and installed it. Still dripping! Any ideas?
lindy46 is offline   Reply With Quote
Old 03-18-2024, 02:52 PM   #2
Camping family
Senior Member
 
Join Date: Sep 2020
Location: Jacksonville
Posts: 993
Did you use plumbers tape around the threads?
__________________
Bob/Kay
Jacksonville, Nc
2020 Keystone Cougar 5th wheel 29 rks traded now
2021 3761 fl Montana 5th wheel
Pulled with a 2022 F350 King Ranch
Retired LEO after 35 years just enjoying life now.
Camping family is offline   Reply With Quote
Old 03-18-2024, 03:00 PM   #3
bobbecky
Senior Member
 
bobbecky's Avatar
 
Join Date: Jul 2013
Location: Box Elder
Posts: 2,910
Your pressure relief valve is working exactly as it should. With the water inlet where you connect city water being a check valve, when the water heater is working, pressure is building up in your plumbing and has no where to go if there wasn't the relief valve, and something would burst. To stop the leaking, you need to drain water from the water heater so the water level is below the relief valve so there is an air pocket in the water heater tamk that can absorb the pressure increase. that will stop the valve from leaking for a while. You will have to do this occasionally as the air disappears, or just ignore the leaking and enjoy camping.
__________________
Bob & Becky
2012 3402 Montana
2012 Chevy 2500HD D/A CC
bobbecky is offline   Reply With Quote
Old 03-18-2024, 03:10 PM   #4
chuckster57
Site Team
 
chuckster57's Avatar
 
Join Date: Jul 2014
Location: Modesto
Posts: 20,357
Quote:
Originally Posted by lindy46 View Post
The pressure relief valve started dripping, so I cleaned and sprayed it with WD40. Still leaked. So I bought a new unit and installed it. Still dripping! Any ideas?
Never spray any oils on/in the potable water system, unless it’s oil fit for human consumption.
__________________

2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.

Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
chuckster57 is offline   Reply With Quote
Old 03-18-2024, 04:52 PM   #5
Ramtop
Member
 
Join Date: Jun 2022
Location: Walpole, NH
Posts: 62
How high is your water pressure coming into the camper? Could be too much pressure
__________________
2019 Ram 2500 Crew Cab 4x4 6.4L Hemi
2014 Keystone Sprinter 269fwrls Copper Canyon
Ramtop is offline   Reply With Quote
Old 03-19-2024, 05:17 AM   #6
lindy46
Member
 
Join Date: Apr 2013
Location: Tennessee
Posts: 65
Quote:
Originally Posted by Camping family View Post
Did you use plumbers tape around the threads?
Not leaking at the threads.
lindy46 is offline   Reply With Quote
Old 03-19-2024, 05:18 AM   #7
lindy46
Member
 
Join Date: Apr 2013
Location: Tennessee
Posts: 65
Quote:
Originally Posted by Ramtop View Post
How high is your water pressure coming into the camper? Could be too much pressure
On the fresh water tank and pump.
lindy46 is offline   Reply With Quote
Old 03-19-2024, 05:24 AM   #8
lindy46
Member
 
Join Date: Apr 2013
Location: Tennessee
Posts: 65
Quote:
Originally Posted by bobbecky View Post
Your pressure relief valve is working exactly as it should. With the water inlet where you connect city water being a check valve, when the water heater is working, pressure is building up in your plumbing and has no where to go if there wasn't the relief valve, and something would burst. To stop the leaking, you need to drain water from the water heater so the water level is below the relief valve so there is an air pocket in the water heater tamk that can absorb the pressure increase. that will stop the valve from leaking for a while. You will have to do this occasionally as the air disappears, or just ignore the leaking and enjoy camping.
I replaced the unit so water level was below level of the valve. After installation, turned water back on with the valve open and when water started coming out, shut the valve. Let it fill then opened and closed valve quickly several times. That is how I've always done it. Didn't leak until water heated up.
lindy46 is offline   Reply With Quote
Old 03-19-2024, 05:32 AM   #9
jxnbbl
Senior Member
 
jxnbbl's Avatar
 
Join Date: Sep 2020
Location: jackson
Posts: 1,122
Quote:
Originally Posted by lindy46 View Post
I replaced the unit so water level was below level of the valve. After installation, turned water back on with the valve open and when water started coming out, shut the valve. Let it fill then opened and closed valve quickly several times. That is how I've always done it. Didn't leak until water heated up.
Even at my house, the only time I use the relief valve with water heater maintenance/replacement is to open it up when draining the tank. I the tub/sink etc the furthest away with the strainer removed to let the air escape. This allows a natural buffer of air to remain in the tank. For an RV I guess I would use the outdoor shower if I didn't want to fill the gray tank. But if there was major plumbing work (replace the HWH) I probably would go through my normal sanitation routine and end up filling the system 2x anyways.

These relief valves leak when the there is no room for the water to expand. It usually when a boiler has a 'relief valve problem' it is a expansion tank bladder problem.
__________________
JXNBBL (Jay)
Jackson, NH
2021 Keystone 330BHS
2023 Ram 3500 6.7L diesel, 3.73 ratio
jxnbbl is offline   Reply With Quote
Old 03-19-2024, 09:27 AM   #10
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,998
Quote:
Originally Posted by lindy46 View Post
I replaced the unit so water level was below level of the valve. After installation, turned water back on with the valve open and when water started coming out, shut the valve. Let it fill then opened and closed valve quickly several times. That is how I've always done it. Didn't leak until water heated up.
The process you are using is contradictory to the process outlined in the Suburban Water Heater Manual. The same process is outlined in the Atwood manual. Essentially, what you are doing is "filling the water heater tank COMPLETELY with water and eliminating the "required air gap" which is the only means for the water heater to allow for expansion as the water heats. So, you are "forcing the relief valve to leak when you turn it on. Steps 5 and 6 in the instructions are "essentially the opposite" of what you say you're doing.

Here's the instructions for establishing an air gap from the Suburban manual. Note that the method used is to open the relief valve to allow the tank to drain below the valve level, then "snap the valve closed" and turn on the water (which forces the air to pressurize at the top of the tank). This air gap should be BELOW the relief valve, so it no longer leaks "water" but only dissipates some of the air from the air gap. As the air gap reduces, then repeat the process to re-establish the air gap. On my water heater, I re-establish the air gap about monthly when the trailer is in use and I always drain the water heater using the anode fitting if the water heater will not be used for more than a couple of weeks. This prevents the water in the tank from continuing to "corrode the porcelain lining". I would do the same on an Atwood water heater because the tank is an aluminum alloy which serves as its own anode (the tank corrodes to protect itself).

Here is the procedure from the Suburban manual:
Attached Thumbnails
Click image for larger version

Name:	SUBURBAN WATER HEATER AIR GAP EXPLANATION.jpg
Views:	36
Size:	159.4 KB
ID:	46431  
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 03-19-2024, 12:04 PM   #11
dutchmensport
Senior Member
 
Join Date: Jan 2013
Location: Indiana
Posts: 2,720
Agree with others.... don't bleed the air out of the water heater by lifting the pressure relief valve. Turn on a hot water faucet somewhere and let the air purge itself out, creating the necessary air pocket at the top of the water heater.

The only time that valve should be flipped open is when draining the tank. Never when filling.
__________________
2019 Montana High Country 375FL
2014 Chevy Duramax HD 6.6 - 3500 Diesel Dully Long bed Crew Cab
dutchmensport is offline   Reply With Quote
Old 03-22-2024, 05:59 AM   #12
lindy46
Member
 
Join Date: Apr 2013
Location: Tennessee
Posts: 65
Quote:
Originally Posted by JRTJH View Post
The process you are using is contradictory to the process outlined in the Suburban Water Heater Manual. The same process is outlined in the Atwood manual. Essentially, what you are doing is "filling the water heater tank COMPLETELY with water and eliminating the "required air gap" which is the only means for the water heater to allow for expansion as the water heats. So, you are "forcing the relief valve to leak when you turn it on. Steps 5 and 6 in the instructions are "essentially the opposite" of what you say you're doing.

Here's the instructions for establishing an air gap from the Suburban manual. Note that the method used is to open the relief valve to allow the tank to drain below the valve level, then "snap the valve closed" and turn on the water (which forces the air to pressurize at the top of the tank). This air gap should be BELOW the relief valve, so it no longer leaks "water" but only dissipates some of the air from the air gap. As the air gap reduces, then repeat the process to re-establish the air gap. On my water heater, I re-establish the air gap about monthly when the trailer is in use and I always drain the water heater using the anode fitting if the water heater will not be used for more than a couple of weeks. This prevents the water in the tank from continuing to "corrode the porcelain lining". I would do the same on an Atwood water heater because the tank is an aluminum alloy which serves as its own anode (the tank corrodes to protect itself).

Here is the procedure from the Suburban manual:
followed the procedure from the Suburban manual and still had some dripping, but it eventually stopped. I'll see what happens.
lindy46 is offline   Reply With Quote
Old 03-22-2024, 07:38 AM   #13
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,998
Quote:
Originally Posted by lindy46 View Post
followed the procedure from the Suburban manual and still had some dripping, but it eventually stopped. I'll see what happens.
If you've got a "well used" pressure relief valve that you've held open repeatedly to fill the tank completely with water, you may have some buildup around the relief valve seal. If so, it may leak until that buildup is broken away (if it's a calcium type solid buildup). So "snapping the relief valve lever" several times while the tank is empty might speed up removal of that buildup.

This is "just a thought" about why your current relief valve may have been leaking when you first established an air gap after not doing so for a prolonged time.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 03-22-2024, 08:31 AM   #14
Dipstick
Gone Traveling
 
Join Date: Mar 2024
Location: home
Posts: 11
Probably needs s new flapper dapper.
Dipstick is offline   Reply With Quote
Old 03-22-2024, 08:37 AM   #15
GlasNav
Senior Member
 
GlasNav's Avatar
 
Join Date: Feb 2022
Location: Onaga, KS
Posts: 466
Replacements are less than $20, as a matter of fact CW presently has them on sale for $16.34
__________________

2021 Cougar 25RDS
2019 RAM 3500 Longhorn, Mega Cab, DRW,
Cummins 6.7 HO, Aisin 6 Spd HD, 4x4
GlasNav is offline   Reply With Quote
Old 03-22-2024, 09:45 AM   #16
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,998
Quote:
Originally Posted by GlasNav View Post
Replacements are less than $20, as a matter of fact CW presently has them on sale for $16.34
In his first post, the OP stated that he bought and installed a new relief valve. What I didn't see through the thread is whether he switch back to the old one when the new one also leaked, when he installed the new one (possibly last year ???) and any indication of which one is currently in the water heater, the old one with WD40 on it or the new one and how old the new one really is....
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 03-22-2024, 09:54 AM   #17
GlasNav
Senior Member
 
GlasNav's Avatar
 
Join Date: Feb 2022
Location: Onaga, KS
Posts: 466
Just reread the OPs posts, in post 12, it stopped leaking!
__________________

2021 Cougar 25RDS
2019 RAM 3500 Longhorn, Mega Cab, DRW,
Cummins 6.7 HO, Aisin 6 Spd HD, 4x4
GlasNav is offline   Reply With Quote
Old 03-22-2024, 10:00 AM   #18
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,998
Yep...

Hopefully establishing the air gap is his "end of problem fix"... If he has issues later on, hopefully he will post that as a follow up in this thread.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 03-22-2024, 11:42 AM   #19
bobbecky
Senior Member
 
bobbecky's Avatar
 
Join Date: Jul 2013
Location: Box Elder
Posts: 2,910
The reason the S/B water heaters don't have the problem like in the RV is that there usually isn't a check valve on the incoming water line, so when the water heater heats up, the excess pressure just backs up some water back into the water line coming from the street. It's the check valve on the RV where you connect your water hose that retains the water and causes the pressure to build up and makes the T&P valve vent pressure when there isn't an air pocket to absorb the expansion.
__________________
Bob & Becky
2012 3402 Montana
2012 Chevy 2500HD D/A CC
bobbecky is offline   Reply With Quote
Old 03-23-2024, 06:48 AM   #20
jxnbbl
Senior Member
 
jxnbbl's Avatar
 
Join Date: Sep 2020
Location: jackson
Posts: 1,122
Quote:
Originally Posted by bobbecky View Post
The reason the S/B water heaters don't have the problem like in the RV is that there usually isn't a check valve on the incoming water line, so when the water heater heats up, the excess pressure just backs up some water back into the water line coming from the street. It's the check valve on the RV where you connect your water hose that retains the water and causes the pressure to build up and makes the T&P valve vent pressure when there isn't an air pocket to absorb the expansion.
Very good point! I never thought about that.
__________________
JXNBBL (Jay)
Jackson, NH
2021 Keystone 330BHS
2023 Ram 3500 6.7L diesel, 3.73 ratio
jxnbbl is offline   Reply With Quote
Reply

Tags
heat, heater, water, water heater


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 03:08 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.